Page Revision: 2008/09/12 02:10
Executive Summary
- Plan to buy a used NEMA style unit. A-B 509 and 709 are good choices, as is the Square D 8536. Furnas, Westinghouse, GE are also popular. With other brands you are less apt to find the heaters you will need.
- Consult a NEMA table to figure out what size starter your motor needs. This is based SOLELY on phase, voltage, and HP.
- Buy a used NEMA style magnetic starter in that size. Don’t worry what size or how many heaters it has, if any. Also make sure the coil voltage on it is a voltage that you will have available in the enclosure it will go into.
- Consult the appropriate heater table to find the right size of heater you need for your model of starter, given your motor’s fully loaded Amps (FLA). Heaters from the major brands are still readily available used.
- If your unit didn’t come with pushbuttons or an enclosure, you’ll need to buy them too.
- Go read the Starter Wiring wiki.
 Allen Bradley Magnetic Starter 709 |
Magnetic Starter Tutorial
You probably wound up here because you need to buy “something” to turn on the motor on your machine, or perhaps you have bought or scrounged a used “something” and realize that you have no idea if it’ll do the job, or maybe you are changing your machine to use a new motor with a different voltage/phase and are not sure if the existing “something” can do the job.
I recently went through the same experience. I bought a new motor with different voltage, phase, and HP specs from the original in my planer, and wound up spending more on a new Magnetic Starter than the motor cost me! That was a rude shock. Second time around I got a bit smarter, understanding more of what I needed, I was able to get what I needed used off eBay for way cheaper.
(Note that there is a
seperate wiki on wiring a magnetic starter, please refer to it for more details on the wiring.)
Let me first state that I am by no means an expert on magnetic starters. Having just recently gone through the experience that you are in the midst of, I hope that by laying out what I learned along the way your path the understanding what you need will be smoother (and cheaper!) than mine was.
I hope that this wiki will serve as a starting point that others with more expertise in the area will add to. If you find any errors or missing information in this wiki, please feel free to make any changes you feel are needed!
Definitions
Relay
Disconnect
You will need a disconnect if your machine is hard wired to the building wiring. This disconnect is a safety to ensure that the machine cannot be turned on when working on it. If your machine is equipped with a plug that you have to plug into a receptacle, this is your disconnect. Disconnect your machine whenever working on it, changing blades, etc. A magnetic starter WILL start the motor regardless of where your hands are if the Disconnect is not used!
Phase
Three phase Starters can be used in single phase applications, but the converse is not normally true, unless it was originally a three phase device used in a single phase situation, then it could be re-purposed to a three phase environment! (Don’t worry, it won’t get any more complicated than this!)
Note that there is some controversy in the forums regarding how many heaters are needed when using a three phase starter in a single phase application. Some feel that only one (the hot) leg needs a heater, others feel both should have one. Some contactors may require all three heaters be in place to function, while the rating and thus proper operation of the heaters may be predicated on all three being present. So bottom line is that heaters are cheap. Use three even if you are single phase and you’ll never have to worry.
Switch
Manual Starter
A manual motor starter usually has 2 or 3 pushbuttons; start, stop and sometimes a separate reset button. Sometimes the reset is combined with the stop button. These starters require mechanical action (you pushing the start or stop button) to close or open the contacts on the starter's contactor. Manual starters usually contain "heaters" which are overload protection devices that will automatically (by mechanical means) open the contacts in the event that the motor draws too much current. The heaters must be sized for the full load operating current of the motor for the voltage that you are operating the motor at. A manual starter will remain on if you have a power failure, so when the power comes back the motor will start without you doing anything, making them inappropriate from a safety perspective for most of our woodworking machinery.
Magnetic Starter
A magnetic starter is similar to a manual starter except that it uses a relay to connect the contacts. The pushbuttons that control this relay are usually low current momentary contact switches. Pushing the start button energizes the relay and starts the motor. There is a "holding" contact on the relay which keeps it energized until something else interrupts the current to the relay such as pushing the stop button or if there is a power failure. You have to press the start button again after a power failure to start the motor. Magnetic starters usually have heaters which function as described in manual starters above.
A Magnetic Starter consists internally of a contactor, heaters, coil and control circuit, pushbuttons, and an enclosure. The pushbuttons may or may not be in the same enclosure, and some or all of the starters components may be integrated together. Sometimes it’s just called a Starter, or a Motor Starter, or a Magnetic Motor Starter. It is NEVER called a Switch.
While we are on the subject, the above assumes that the control station is wired as a "three wire" control. This is typical and is what is shown on the
Wiring Wiki but Magnetic Starters can be controlled in other ways, some of which DO NOT provide the No-Restart safety feature. If you are looking at an unknown piece of equipment, it is best to verify this before relying on it. Be Safe, Not Sorry!
Contactor
This is the heart of the Magnetic Starter. I like to think of it as a hopped-up relay. It’s the part that closes the circuit to your motor, allowing current to flow and the motor to run. It has a set of contacts for controlling the power to the motor, normally three, sometimes two. It also has a coil, such that when power is applied to the coil by the Auxilliary Circuit, it will cause the contacts to close. Sometimes the contactor is incorrectly referred to as a Starter. It is only one component of a starter. This misleading description is common on eBay.
Heater
Also called Thermal Overloads, Thermal Overload Relays, Overload Heaters, or simply Overloads. These are basically simple heat sensitive circuit breakers that are matched to the current draw of the motor, and plug into or otherwise attach to the contactor. They will trip if their temperature rises above a certain level, due to excessive current passing through them. Heaters sense current, not voltage.
They may seem redundant, after all you have a circuit breaker box in your house/shop that protects everything, so why do you need another? The reason is the circuit breakers in your house are designed to protect the wiring in your house, and by extension the house itself. The heaters in your Magnetic Starter are designed to protect your motor. Heaters are designed to mimic the characteristics of a motor in use(“eutectic”) and have similar heating characteristics. Motors can tolerate short term overloads without damage. These overload conditions can persist far longer than a typical circuit breaker or fuse can tolerate at a similar condition, that’s why we use heaters instead of a similarly sized fuse or circuit breaker. You want your heater to trip the overload before you smoke the motor!
 Different AB Heater Styles (Class 10, 20, and 30) |
 Furnas Heater |
Control Circuit
Be aware that coils are available in several different voltages (24v, 120v, 208v, 240v, 440v, 575v, etc.). You will need to provide the appropriate voltage to run your coil or the starter will be of no use. Most coils are replaceale, but they can be hard to locate and expensive. Coil voltages lower than your supply voltage are easily created with a step-down transformer, but coil voltages higher than your supply voltage are more difficult to generate. Transformers are also an added expense, slightly complicate the wiring and take up valuable space in, or on, the starter.
Pushbuttons
A Magnetic Starter typically will have ON and OFF pushbuttons, sometimes a Reset too. These are part of the Control Circuit. These will be momentary contact, ON being Normally Open and OFF being Normally Closed. Momentary contact means that contact is made only as long as the button is pushed. This is quite different from a light switch, where the contact remains in position until the switch is flipped again. No need to hold the light switch in position for the lights to remain on. . . (the auxiliary contacts on the relay provides the latching function for the control circuitry so the motor stays on after you release the ON button)
 Separate Pushbutton Station |
 Older Enclosure With Integrated Pushbuttons |
The Coil “Thing”
The coil is a key component of a Magnetic Starter. Electrically, it is part of the Control Circuit, in fact it is what the control circuit controls. Physically, it is located in the contactor. Contactors are rarely ever sold without a coil in them. When you push the “ON” button, the contactor’s coil is energized, causing the contacts in the contactor to close. At the same time a separate smaller relay sometimes called the auxiliary contact or auxiliary relay is also energized. This relay is electrically in parallel with the “ON” button and stays closed when you release the “ON” button, keeping the coil energized and thus the main contacts closed. Similarly, when you push the “OFF” button, the auxiliary contact is de-energized and opens, causing the coil to be de-energized, and the main contacts to open and the motor to coast to a stop. The auxiliary circuit uses only a small amount of current, and is separate from the main circuit.
The key thing to understand is that a coil is rated at a specific voltage. So when you buy your starter, make sure the coil has the right voltage. Usually “the right voltage” means the same voltage as the motor. One exception might be in a 240V situation, if the neutral line is also brought into the enclosure, then 120V will be available so either a 240V or 120V coil would work. (Never use ground in place of neutral.) Another exception would be if the pushbuttons are to be really remote from the rest of the Starter, 24V might be a safer choice.
NEMA
IEC
The IEC is the International Electrotechnical Commission. This is another specification for Magnetic Starters, very popular in Europe and now in Asia. Most of the cheap Chaiwan machines use IEC starters on them. In fairness, companies like Siemens and Moeller make good quality IEC starters. NEMA and IEC do not directly cross match. It’s not like pounds and kilograms or Farenheight and Celcius. IEC spec starters may not have heaters, rather Instead of heaters, the overcurrent rating can be adjusted within the specified range of the device, via a built-in potentiometer type control.
A very good explanation of the differences between IEC and NEMA can be found
here.
Many OWWM’ers prefer the more robust NEMA style, and think they look more appropriate on the older machines. However, new NEMA starters are not cheap. Oftentimes an import IEC Starter will be available at a very appealing price. But, there are
http://www.sawmillcreek.org/showthread.php?t=71086 with these inexpensive Starters.
One OWWMer summed up his experiences with IEC starters as “I would not trust them as far as I can throw them. And I have thrown them.”
Obviously, it safely starts up the machine. And, it does this is such a way that it minimizes arcing of the contacts, and danger to the operator. A ‘switch’ as we commonly know it would be destroyed quickly by the arcing caused by the high start up currents of our motors. To minimize arcing a starter uses a low current control circuit to turn the contactor on quickly, and also the physical area of the contacts is large, further reducing arcing.
It will also protect your motor from drawing too much current. For example: If your motor draws 9 or 10 amps and it gets a jam, low voltage condition, or other anomaly, it has to sit there locked up till the amps get high enough to trip the circuit breaker that is in the main panel. By that time the motor might be fried. The heaters in the motor starter are sized according to the amps the motor draws. They monitor the current flow so if the amps go up even slightly they will open a set of contacts and shut off the motor.
Another important task that the Magnetic Starter does is when power is interrupted for any reason, heater-overload, lightning, plug pulled, power outage, etc, it will automatically ‘turn off’ and prevent the machine from restarting when power re-appears. In other words, the switch STAYS off until the
operator physically turns it on again. (Note that a manual starter will not do this, a crucial difference.)
Another advantage is that the pushbuttons may be mounted remotely from the starter itself.
 Example Motor Specs |
These will be your Chaiwanese built IEC units. Go to the Grizzly website for example, search for Magnetic, have a chuckle that they are called “Magnetic Switches”, then select the ones that are rated for your requirements. They have the exact units you will need, single phase starters rated for 220V (same as 230V) and 3 HP. You are good to go until they stop working.
They have cheesy, flimsy plastic boxes that are hard to mount without a little support rigging. If you try to get too low on the heater amp adjustment, they may cut out. Mid range and up, they work fine and last if you never smack one hard turning around with a long 4 x 4 or the like.
I Want a Used NEMA Starter
There are several steps you need to take in the process of finding the right starter for your situation. Be aware that, as with anything bought used, there is the chance that it might not work. In that case, unless the buyer offers returns, then you will be out of luck. That being said, these old contactors are well built and the biggest problem typically is the contacts can wear due to arcing, and are thus in need of polishing or rarely, replacement.
NEMA starters (actually just the contactors) are selected based on phase, voltage and HP only. You can use
NEMA tables to help you decide what you need. For three phase, select the “Full Voltage Starting” column.
Step 2 – Find a NEMA 1 Unit
Power Equipment Sales Company, and
Mag-trol (ask for Lars),
CPI Surplus and
Automation Direct are also popular suppliers. They can probably find a complete NEMA unit to meet your requirements.
You will quickly notice that your ebay searches will turn up a wide variety of sizes, ages, and styles (IEC/NEMA) of units. As one OWWM’er put it “the dizzying array of manufacturers and models is, well, dizzying”. Some units will be more complete than others, as will the information and photographs provided by the seller. It is unlikely that you will find a complete unit with the correct size heaters for your application. That’s OK, heaters are cheap and readily available. It is more important that you select a proper NEMA size unit for your application (in our example’s case, NEMA 1) and with a suitable coil voltage (240V preferred, 120V OK).
The A-B 500 series (“Bulletin 509 Starters” in the A-B nomenclature) numbering system is explained
here. The Model number will give you an indication of how the starter was supplied from the factory, but many parts can get changed, added, removed, etc. over time. Note that many starters which were originally supplied with enclosures are offered for sale after being removed from the enclosure. Also notice that NEMA specifies enclosure “type” as well as contactor size, but the type is generally not important to OWWM’ers.
So here is a starter that might be suitable for our example motor. It’s a NEMA size 1 with three N-14 heaters and a 120V coil. It also includes the pushbutton, and an enclosure painted back in the day by a 3 year old with fingerpaints. This is nice because it includes everything we need, except that the heaters are the wrong size, and the paint is not to everyone’s tastes. That’s OK, heaters are cheap and readily available.
Notice that the heaters kind of hang off the side of the contactor. This is typical for the A-B units.
 Complete A-B Starter |
 A-B Starter Detail Showing Coil Specs |
 A-B Starter Enclosure |
To choose heaters you need to know what contactor you will be using. In this example, it’s an A-B 709 series. You can see from looking at the pictures that it comes with N-14 heaters. We can consult a heater table such as the one
http://www.southlandelectrical.com/AllenBradlyHeaterTables.asp?url=IND for the A-B “N” series to determine that the N-14 heater in a NEMA 1 starter are rated for only 1.98 Amps. Clearly this is inadequate for the 19 Amp motor! The same table shows that for 19 Amps an N-38 heater will be required. A search on eBay shows heaters available from numerous suppliers for under $3 each.
So our work is done here. Time to consult the wiring wiki!
I Have This Old Starter I Scrounged Up , Can I use it?
Unless you are remarkably lucky, the heaters that came with the starter you scrounged up will probably not be the right size. Whether it came with heaters or not doesn’t really matter, you should expect to have to buy the right size ones.
What about the coil, is it a voltage that you can supply? If it’s a 440V coil you are looking at some extra work/cost that can be easily avoided by using a different coil or a unit with a different coil. Luckily, most used starters for sale these days seem to come with 240V or 120V coils.
Don’t forget you’ll need pushbuttons and an enclosure too!
Here’s one example.
 MTE IEC Type Starter |
It came from a jointer that used this motor on it. It’s a 575V 3 phase 5 HP motor that draws 5.6 Amps.
 WEG Motor Plate |
In addition, the contactor is wired for 575V control, so even if the contactor and overload were suitable for the current of the 240V motor, it is unlikely that the coil would work at 240V. A transformer could be used to step up from 240V to 575V, but you will note that there is no space in the enclosure for a transformer.
Other Example Starters
Here’s another AB unit. It’s a NEMA size 2 and has what look like three N-33 heaters on it. Can’t tell from the photo what the coil voltage is, the red printing that is obscured by the camera flash would normally show it, but red printing on an AB starter means a 120V coil (208v is black, 240v is green). Also, there is no pushbutton or enclosure with this unit.
 A-B NEMA Size 2 Starter |
Here is a Westinghouse NEMA size 0 unit. It has three FH27 heaters on it. Notice that they are positioned directly below the contactor like an AB 509 rather than to the side as are the AB 709 heaters. It does not have the coil voltage printed on it, but the vendor helpfully states “I assume that the coil is 230 Volt because that was the voltage it was hooked up to”. Remember, Caveat Emptor - Buyer Beware. There is no guarantee that this coil is 230 volt.
 Westinghouse NEMA Size 0 Starter |
 Cutler-Hammer NEMA Size 0 Starter) |
Here is a GE starter. This one is interesting because it only includes two heaters, the place where the third heater would normally go is simply shorted. Vendor states it is NEMA size 1, has a 120V coil, and gives the heater size. Possibly used in a 120V single phase application, got away with only two heaters instead of three. Again, pushbutton and enclosure are not included.
 GE NEMA Size 1 Starter |
 Square D NEMA Size 0 Starter |
Here is a more modern Cutler Hammer starter. It shows clearly on it that it is NEMA size 0. It has three heaters which may be set to one of four current settings. Kind of a transitional type of heater between the single value heaters of old, and the potentiometer adjustable heaters on today’s starters.
 Cutler-Hammer NEMA Size 0 Starter |
Other Issues
Heater Class
A-B Heater Interchangeabilty
NEMA Style
While NEMA size refers to the electrical “size” of the contactor as described in the previously referenced
NEMA tables, NEMA style refers to the size of enclosures used to house Starters.