Page History: Motor Starter Wiring Diagrams
Page Revision: 2011/01/23 07:54
Be Careful! The information presented below is a collaborative effort by several people. The people providing this information may or may not be providing completely accurate information. The information may or may not be relevant to your situation or particular equipment and may or may not comply with local codes. The information should be used as a reference source only. If you are not sure about anything presented, please do not risk your safety, property or life. Hire an electrician.What is a Motor Starter?
Motor Starters are switches specially designed for starting motors. These switches are designed to withstand the larger loads required by motors. There are basically two types of motor starters, Manual Starters and Magnetic Starters.
Motor Starters serve two main purposes:
- The relay contacts are heavy duty and are rated for the motor starting current.
- Service Panel circuit breakers are designed to protect building wiring, not motors plugged into wall receptacles. If your electrical box circuit breaker trips before your motor burns up, it is incidental, not on purpose. However, motor starters are designed to trip on heater overload before the motor they start burns up.
Manual Motor Starters
Manual motor starters are simply manual switches designed to control larger current loads typical of motor control. They may be small and similar to the light switches in your home, or they may be much larger dedicated switches designed for control of high amperage circuits. These motor starters may be either Single Pole (switch one line only) or Double/
Triple Pole devices (switch 2/3 lines). When a Double/Triple Pole manual motor starter is turned off, the power from the power cable is completely disconnected from the motor. Manual motor starters may also be equipped with matched heaters, which are overload protectors designed to open when the current load is too high. These heaters must be properly sized to the motor they are protecting or else they will either open too soon, or will not protect the motor. The disadvantage to manual motor controls is that they cannot have remotely located On and Off controls.
DO NOT USE LIGHT SWITCHES TO START MOTORS
Manual Starter? Follow the wiring sequence as below and merely ignore the control wiring in RED.
There are single pole starters that should only be used for 120 volt motors. L1 is Line 1 in and should be the "hot" black wire. T1 is Motor 1 out and goes from the starter to the motor. In this case, Neutral "White" is carried through to the motor bypassing the starter altogether. This wiring should not be used on 240 volt circuits.
240 volt, 1 phase motors should use a 2 pole starter. L1 is Line 1 in and should be connected to one of the "hot" wires, L2 is Line 2 in and should be connected to the other "hot" wire. T1 and T2 are the corresponding motor out connections and should be carried through to the motor.
Three Phase motors require 3 pole starters and each of the "hot" lines must be switched through the starter.
Magnetic Motor Starters
Magnetic Motor starters are essentially heavy duty relays, often equipped with heater/thermal overloads matched to the motor they start. They are then controlled using a lighter duty (low or high voltage) circuit, auxillary relay contacts and a control station (or several stations) utilizing lighter duty switches (usually momentary sometimes latching). These switches would not be capable of switching the large loads required by the motors. Because the control circuitry is separate from the Load circuit, the On/
Off controls can be mounted remotely and can even be duplicated if desired.
This type of motor starter will usually have an auxiliary contact switch: a smaller set of contacts that opens or closes along with the motion of the main contactors. These contacts will be used to latch the system in an on condition (contacts shown in the picture below as 2-||-3). Latching means that the auxiliary contact bypasses the ON button so the solenoid remains energized, until a separate OFF button cuts the power. Additional contacts (NO & NC) may also be provided and may be used for auxiliary circuits or to provide feedback to the rest of the system that the starter is engaged and the motor has power.
Some older style motor starters have built-in latching. These starters have four terminals labeled 3, P, E, and C (historical leftovers from older models). The E and C terminals are for the hot and neutral wires, respectively, and remain powered. When power is applied to 3 and P at the same time, the starter will engage until power is removed from P. Power can be removed from 3 at any time without affecting operation. The wiring for these starters is not addressed below............
TYPICAL WIRING
Connector numbers will vary among manufacturers - typical numbers in brackets().
- L1 (1) - first line in from power source (phase 1 for 3ph / Neutral for 1ph)
- L2 (3) - second line in from power source (phase 2 for 3ph / Hot for 1ph* see below for alternate wiring using L2 & L3)
- L3 (5) - third line in from power source (phase 3 for 3ph / NC for for 1ph)
- T1 (2) - first line out to motor (phase 1 for 3ph / Hot for 1ph)
- T2 (4) - second line out to motor (phase 2 for 3ph / NC for 1ph* see below for alternate wiring)
- T3 (6) - third line out to motor (phase 3 for 3ph / Neutral for 1ph)
- -||- (1-2, 13-14, 53-54)is a normally Open NO contact (closes when the relay energizes)
- -|/|- (95-96) is a normally closed NC contact (opens when the thermal overloads trip if associated with the overload block - as shown in all three diagrams)
- -|/|- is a normally closed NC contact (opens when the relay energizes if associated with the relay coil as auxiliary circuit - as shown in the motor reversing diagram as coil isolation contacts)
- M - Relay Coil
Duplicating Controls
- START Button must be wired in Parallel to one another
- STOP Buttons must be wired in Series with each other
NOTES:- Low Voltage Control with transformer - The transformer output must be rated at the appropriate value for the relay coil (typically 12 or 24 VAC) in your particular starter. This should not be an issue with a manufactured magnetic motor starter as the transformer will have been chosen by the manufacturer to match the coil. Input power for the transformer comes from two legs of the primary input power, chosen to match the input voltage requirements of the transformer.
- Line Voltage Control without transformer - Magnetic Motor Starters which have relay coils at line power levels do not use transformers. Power for the starter relay is taken from two legs of the primary input power, chosen to match the input voltage requirements of the relay coil.
- In either case, power should be taken from below the manual disconnect (if used). This will ensure that there is no power in the box once the manual disconnect has been thrown.
- All diagrams are intended to illustrate the logic of a latching contol circuit. Your motor starter may use wiring which is internal to the starter, wiring which is different than the diagrams, etc. Please refer to the manufacturer's literature if in doubt.
If you are not sure of how to make the connections on your equipment, hire an electrician. Improper wiring can Kill, Injure, Start Fires, Burn Out Motors or any/all of the above.3ph Starter/3ph Motor
Line Voltage Control three phase (3ph) motor starter controlling a three phase motor (rev 08 Aug 2006)
Manual Starter? Merely ignore the control wiring in
RED3ph Starter/1ph Motor
Line Voltage Control three phase (3ph) motor starter controlling a single phase motor (rev 08 Aug 2006)
Some 3 phase Magnetic Motor Starters require current to be seen across each of the three overloads. This may be accomplished by directing the output of second circuit back into the input of the third (previously unused) circuit and feeding the motor off of the output of the third circuit (rather than the second). Wiring then becomes:
Line 1 → L1 → T1 → Motor 1 (L1-hot
240v or neutral
120v)
Line 2 → L2 → T2 → L3 → T3 → Motor 2 (L2-hot
120v or 240v)
RED3ph Starter/3ph Motor/Reversible
Line Voltage Control - double contactor three phase motor starter controlling a reversible three phase motor (rev 08 Aug 2006)
(Note: L1 becomes T3 and L3 becomes T1 when the reverse relay is actuated.)
The motor must be STOPPED before REVERSING unless the contactor allows for on-the-fly reversing. The coils are locked out via the NC contacts (M1, M2) usually contained within the mechanical interlock. When Coil #M1 is engaged, Coil #M2 is locked out and vice-versa.
Magnetic Starter - Control Stations
One of the advantages of magnetic starters is the ability to add control stations. These stations may be located at any convenient location and duplicated as required. The maximum number of stations and their location is unlimited for all practical purposes. Stations are built using Normally Closed (STOP) and Normally Open (START) momentary contact switches. These switches must be rated for the control circuit voltage at a minimum. Over-rated switches will work fine. Many manufacturers incorporate both Normally Open (NO) and Normally Closed (NC) contacts in a single switch body. By rewiring the switch you can change it from one to the other. Many manufacturers also provide interchangeable buttons in at least red and green.
The last station must always be provided to complete the circuit. The intermediate stations may be repeated as many times as required. Suitable 3 conductor control wiring is required from the starter to each of the control stations in turn (daisy chained).
NEMA Starter Size Charts
