Magnetic Starters
Modified on 2018/08/20 21:17 by bullmastiff — Categorized as: Electrical
Article by Dan McCallum
Executive Summary
  1. Plan to buy a used NEMA style unit. A-B 509 and 709 are good choices, as is the Square D 8536. Furnas, Westinghouse, GE are also popular. With other brands, or more obscure models, you are less apt to find the heaters you will need.
  2. Consult a NEMA table to figure out what size starter your motor needs. This is based SOLELY on phase, voltage, and HP.
  3. Buy a used NEMA style magnetic starter in that size. Don’t worry what size or how many heaters it has, if any. Also make sure the coil voltage on it is a voltage that you will have available in the enclosure it will go into.
  4. Consult the appropriate heater table to find the right size of heater you need for your model of starter, given your motor’s fully loaded Amps (FLA). Heaters from the major brands are still readily available used.
  5. If your unit didn’t come with pushbuttons or an enclosure, you’ll need to buy them too.
  6. Go read the Starter Wiring wiki.
Allen Bradley Magnetic Starter 709
Magnetic Starter Tutorial
You probably wound up here because you need to buy “something” to turn on the motor on your machine, or perhaps you have bought or scrounged a used “something” and realize that you have no idea if it’ll do the job, or maybe you are changing your machine to use a new motor with a different voltage/phase and are not sure if the existing “something” can do the job. I recently went through the same experience. I bought a new motor with different voltage, phase, and HP specs from the original in my planer, and wound up spending more on a new Magnetic Starter than the motor cost me! That was a rude shock. Second time around I got a bit smarter, understanding more of what I needed, I was able to get what I needed used off eBay for way cheaper.
(Note that there is a Wiki separate wiki on wiring a magnetic starter, please refer to it for more details on the wiring.)
Let me first state that I am by no means an expert on magnetic starters. Having just recently gone through the experience that you are in the midst of, I hope that by laying out what I learned along the way your path the understanding what you need will be smoother (and cheaper!) than mine was. I hope that this wiki will serve as a starting point that others with more expertise in the area will add to. If you find any errors or missing information in this wiki, please feel free to make any changes you feel are needed!
Definitions
Relay
A contactor will often be fitted with auxiliary relay contacts as well. One set of tehse will be used to latch the contactor in the ON position after pressing the On button on the control station. These auxiliary contacts, available in both Normally Open (NO) and Normally Closed (NC) can also be used to control other equipment such as a dust collections system, lights, etc.
Disconnect
You will need a disconnect if your machine is hard wired to the building wiring. This disconnect is a safety to ensure that the machine cannot be turned on when working on it. If your machine is equipped with a plug that you have to plug into a receptacle, this is your disconnect. Disconnect your machine whenever working on it, changing blades, etc. A magnetic starter WILL start the motor regardless of where your hands are if the Disconnect is not used!
Phase
Three phase Starters can be used in single phase applications, but the converse is not normally true.
Note that there is some controversy in the forums regarding how many heaters are needed when using a three phase starter in a single phase application. Some feel that only one (the hot) leg needs a heater, others feel both should have one. Some starters may require all three heaters be in place to function, while the rating and thus proper operation of the heaters may be predicated on all three being present. So bottom line is that heaters are cheap. Use three even if you are single phase and you’ll never have to worry.
Switch
Manual Starter
A manual motor starter may be equipped with pushbuttons, a toggle or even a rotary switch mechanism. These starters require mechanical action (you pushing the start or stop button) to close or open the contacts on the starter's contactor. Manual starters may contain "heaters" which are overload protection devices that will automatically (by mechanical means) open the contacts in the event that the motor draws too much current. The heaters must be sized for the full load operating current of the motor for the voltage that you are operating the motor at. Manual motor starters equipped with overload protection will include a reset of some sort. Often, switching the switch to the off position will reset the thermal overload. Sometimes the reset is combined with the stop button. Except for a shut down due to the tripping of a heater, manual starter will remain on if you have a power failure. This means that when the power comes back the motor will start automatically, making them inappropriate from a safety perspective for any machinery where this is an undesirable situation. If you do have a power loss with a machine equipped with a manual starter, you must remember to turn it off immediately.
Magnetic Starter
A magnetic starter is similar to a manual starter except that it uses a relay to connect the contacts. The control station that controls this relay are usually low current momentary contact switches. Pushing the start button energizes the relay and starts the motor. There is a "holding" contact on the relay which keeps it energized until something else interrupts the current to the relay such as pushing the stop button or if there is a power failure. You have to press the start button again after a power failure to start the motor. Magnetic starters usually have heaters which function as described in manual starters above. These heaters may self reset or they may require manual intervention to reset after being tripped.
A Magnetic Starter consists of a contactor, heaters, coil, control station pushbuttons, and an enclosure. The control station pushbuttons may or may not be in the same enclosure, and some or all of the starters components may be integrated together. Sometimes it’s just called a Starter, or a Motor Starter, or a Magnetic Motor Starter. It is NEVER called a Switch.
While we are on the subject, the above assumes that the control station is wired as a "three wire" control. This is typical and is what is shown on the Wiring Wiki but Magnetic Starters can be controlled in other ways, some of which DO NOT provide the No-Restart safety feature. If you are looking at an unknown piece of equipment, it is best to verify this before relying on it. Be Safe, Not Sorry!
Contactor
This is the heart of the Magnetic Starter. I like to think of it as a hopped-up relay. It’s the part that closes the circuit to your motor, allowing current to flow and the motor to run. It has a set of contacts for controlling the power to the motor, normally three, sometimes two. It also has a coil that when energized by the control circuit will cause the motor contacts to close. Sometimes the contactor is incorrectly referred to as a Starter. It is only one component of a starter. This misleading description is common on eBay.
Heater
Also called Thermal Overloads, Thermal Overload Relays, Overload Heaters, or simply Overloads. These are basically simple current sensitive circuit breakers that are matched to the current draw of the motor, and plug into or otherwise attach to the contactor. They will trip if their temperature rises above a certain level, due to excessive current passing through them. Heaters sense current, not voltage. Once tripped, current to the contactors coil is interrupted which causes the primary motor contacts to open and the motor to stop.
They may seem redundant, after all you have a circuit breaker box in your house/shop that protects everything, so why do you need another? The reason is the circuit breakers in your house are designed to protect the wiring in your house, and by extension the house itself. The heaters in your Magnetic Starter are designed to protect your motor. Heaters are designed to mimic the characteristics of a motor in use and have similar heating characteristics. Motors can tolerate short term overloads without damage. These overload conditions can persist far longer than a typical circuit breaker or fuse can tolerate at a similar condition, that’s why we use heaters instead of a similarly sized fuse or circuit breaker. You want your heater to trip the overload before you smoke the motor!
Different AB Heater Styles (Class 10, 20, and 30)
Furnas Heater
Furnas Heater
Control Circuit
Be aware that coils are available in several different voltages (24v, 120v, 208v, 240v, 440v, 575v, etc.). You will need to provide the appropriate voltage to run your coil or the starter will be of no use. Most coils are replaceable, but they can be hard to locate and expensive. Coil voltages lower than your supply voltage are easily created with a step-down transformer, but coil voltages higher than your supply voltage are more difficult to generate. Transformers are also an added expense, slightly complicate the wiring and take up valuable space in, or on, the starter. The advantage of using low voltage control is evident when using many control stations, at the blast gates of a dust collection system for example. Furnas LVC starters have an integral step-down transformer allowing them to be used in many different voltage applications.
Control Stations (Pushbuttons)
A Magnetic Starter typically will have at least one pair of ON and OFF pushbuttons, sometimes a Reset too. These are part of the Control Circuit. These will be momentary contact, ON being Normally Open and OFF being Normally Closed. Momentary contact means that contact is made only as long as the button is pushed. This is quite different from a light switch, where the contact remains in position until the switch is flipped again. No need to hold the light switch in position for the lights to remain on. . . (the auxiliary contacts on the relay provides the latching function for the control circuitry so the motor stays on after you release the ON button)
Separate Pushbutton Station
Older Enclosure With Integrated Pushbuttons
The Coil
The coil is a key component of a Magnetic Starter. Electrically, it is part of the Control Circuit, in fact it is what the control circuit controls. Physically, it is located in the contactor. Contactors are rarely ever sold without a coil in them. When you push the “ON” button, the contactor’s coil is energized, causing the contacts in the contactor to close. At the same time a separate set of auxiliary contacts is also closed. This set of contacts is usually wired to keep the coil energized and thus the main contacts closed even after the Start/On button is released. Similarly, when you push the “OFF” button, the auxiliary contact circuit is interrupted and the coil is de-energized opening the main contacts.
The key thing to understand is that a coil is rated at a specific voltage. So when you buy your starter, make sure the coil has the right voltage for your application. Usually “the right voltage” means the same voltage as the motor. One exception might be in a 240V situation, if the neutral line is also brought into the enclosure, then 120V will be available so either a 240V or 120V coil would work. (Never use ground in place of neutral.) Another exception would be if the pushbuttons are to be really remote from the rest of the Starter, 24V might be a safer choice.
NEMA
IEC
International Electrotechnical Commission. The IEC has also defined a set of standards for, amongst other devices, electric motor starters. IEC rated devices are very common in Europe and Asia and are becoming more prevalent in North America, especially on imported machinery. IEC starters are also available with many features not available on NEMA starters. They are often smaller than comparable NEMA starters and DIN rail compatible making them good candidates for automation control systems. IEC spec starters may not have discrete heaters, but rather use adjustable current blocks. These function in exactly the same manner as a discrete heater with the added advantage that the current rating can be adjusted within the specified range of the device rather than having to obtain new heater elements. Unfortunately, the specified range of the device is usually fairly small.
A very good explanation of the differences between IEC and NEMA can be found here.
Many OWWM’ers prefer the more robust NEMA style, and think they look more appropriate on the older machines. However, new NEMA starters are not cheap, but they are more plentiful on the surplus market. High quality IEC starters are also available at often very high prices. While there does not seem to be as many IEC starters on the surplus market, there are many low quality IEC Starters on the market at a very appealing prices. As with anything, a low initial price may not be a cheaper alternative in the long run.
Obviously, it safely starts up the machine. And, it does this is such a way that it minimizes arcing of the contacts, and danger to the operator. A ‘switch’ as we commonly know it would be destroyed quickly by the arcing caused by the high start up currents of larger motors. To minimize arcing a starter uses a low current control circuit to turn the contactor on quickly, and also the physical area of the contacts is large, further reducing arcing.
If the starter (manual or magnetic) is equipped with thermal overloads or heaters, it will also provide a line of defense intended to protect your motor from drawing too much current. In the case of a high current draw, the heaters will break the circuit and shut the motor off, hopefully before any damage has been done.
Another desirable feature of a Magnetic Starter does is that when power is interrupted for any reason, heater-overload, plug pulled, power outage, etc, the machine shuts off. When power is restored, the machine will stay in the off condition until the operator turns it back on. This is only true of a magnetic starter wired with momentary contact control stations (3-wire control). If a magnetic starter is wired with latching contacts (2-wire control), this feature is lost. (Note that a manual starter will remain in the on position after a power loss, except if power loss was due to a thermal overload condition. Upon restoration of power, the machine will continue to run - this is a crucial difference.)
Another advantage is that the control stations may be mounted remotely from the starter itself. In addition, a single starter may have more than one control station allowing emergency stops, for example, to be located at several different positions.
Example Motor Specs
Example Motor Specs
If purchasing new, these will likely be IEC units. IEC units are available with different coil voltages and current ranges. Pick one suitable for the motor you wish to control. If you look around, you may be able to find a used NEMA starter for the same money.
I Want a Used NEMA Starter
There are several steps you need to take in the process of finding the right starter for your situation. Be aware that, as with anything bought used, there is the chance that it might not work or might be incorrect for your application. In that case, unless the buyer offers returns, then you will be out of luck. That being said, these old contactors are well built and the biggest problem typically is the contacts can wear due to arcing, and are thus in need of polishing or rarely, replacement. Be aware, it may be very difficult to locate parts to rebuild or repurpose an old, obsolete NEMA starter.
NEMA starters (actually just the contactors) are selected based on phase, voltage and HP only. You can use NEMA tables to help you decide what you need. For three phase, select the “Full Voltage Starting” column.
Step 2 – Find a NEMA 1 Unit
Power Equipment Sales Company, and Mag-trol (ask for Lars), CPI Surplus and Automation Direct are also popular suppliers. They can probably find a complete NEMA unit to meet your requirements.
You will quickly notice that your eBay searches will turn up a wide variety of sizes, ages, and styles (IEC/NEMA) of units. As one OWWM’er put it “the dizzying array of manufacturers and models is, well, dizzying”. Some units will be more complete than others, as will the information and photographs provided by the seller. It is unlikely that you will find a complete unit with the correct size heaters for your application. That’s OK, heaters are cheap and readily available for many starters. It is more important that you select a proper NEMA size (in our example’s case, NEMA 1) and with a suitable coil voltage for your application.
The A-B 500 series (“Bulletin 509 Starters” in the A-B nomenclature) numbering system is explained here. The Model number will give you an indication of how the starter was supplied from the factory, but many parts can get changed, added, removed, etc. over time. Note that many starters which were originally supplied with enclosures are offered for sale after being removed from the enclosure. Also notice that NEMA specifies enclosure “type” as well as contactor size, but the type is generally not important to OWWM’ers.
So here is a starter that might be suitable for our example motor. It’s a NEMA size 1 with three N-14 heaters and a 120V coil. It also includes the control station pushbutton, and an enclosure. This is nice because it includes everything we need, except that the heaters are the wrong size, and the paint is not to everyone’s tastes. That’s OK, heaters are cheap and readily available.
Notice that the heaters kind of hang off the side of the contactor. This is one configuration, but the heaters may also be located below the contactor, or even remote from the body.
Complete A-B Starter
 A-B Starter Detail Showing Coil Specs
 A-B Starter Enclosure
To choose heaters you need to know what contactor you will be using. In this example, it’s an A-B 709 series. You can see from looking at the pictures that it comes with N-14 heaters. We can consult a heater table such as the one here for the A-B “N” series to determine that the N-14 heater in a NEMA 1 starter are rated for only 1.98 Amps. Clearly this is inadequate for the 19 Amp motor! The same table shows that for 19 Amps an N-38 heater will be required. A search on eBay shows heaters available from numerous suppliers for under $3 each.
So our work is done here. Time to consult the Motor Starter Wiring Wiki.
I Have This Old Starter I Scrounged Up , Can I use it?
Unless you are remarkably lucky, the heaters that came with the starter you scrounged up will probably not be the right size. Whether it came with heaters or not doesn’t really matter, you should expect to have to buy the right size ones. What about the coil, is it a voltage that you can supply? If it’s a 440V coil you are looking at some extra work/cost that can be easily avoided by using a different coil or a unit with a different coil. Luckily, many used starters for sale will come with 240V or 120V coils. If you receive one with a 24V coil, you will need to use a suitable transformer to obtain 24V for the controls.
Don’t forget you’ll need a control stations (pushbuttons) and an enclosure too!
Here’s one example.
MTE IEC Type Starter
This motor came from a jointer. It’s a 575V 3 phase 5 HP motor that draws a maximum of 5.6 Amps.
WEG Motor Plate
WEG Motor Plate
In addition, the contactor is wired for 575V control, so even if the contactor and overload were suitable for the current of the 240V motor, the coil voltage makes it unsuitable for this application. A transformer could be used to step up from 240V to 575V, but you will note that there is no space in the enclosure for a transformer.
Other Example Starters
Here’s another AB unit. It’s a NEMA size 2 and has what look like three N-33 heaters on it. Can’t tell from the photo what the coil voltage is, the red printing that is obscured by the camera flash would normally show it, but red printing on an AB starter means a 120V coil (208v is black, 240v is green). Also, there is no control station or enclosure with this unit. These would have to be sourced separately.
A-B NEMA Size 2 Starter
Here is a Westinghouse NEMA size 0 unit. It has three FH27 heaters on it. Notice that they are positioned directly below the contactor like an AB 509 rather than to the side as are the AB 709 heaters. It does not have the coil voltage printed on it, but the vendor helpfully states “I assume that the coil is 230 Volt because that was the voltage it was hooked up to”. Remember, Caveat Emptor - Buyer Beware. There is no guarantee that this coil is 230 volt.
Westinghouse NEMA Size 0 Starter
Cutler-Hammer NEMA Size 0 Starter)
Here is a GE starter. This one is interesting because it only includes two heaters, the place where the third heater would normally go is simply shorted. Vendor states it is NEMA size 1, has a 120V coil, and gives the heater size. Possibly used in a 120V single phase application where only a single heater (two heaters optional) are required. Again, the control station and enclosure are not included.
GE NEMA Size 1 Starter
Square D NEMA Size 0 Starter
Here is a more modern Cutler Hammer starter. It shows clearly on it that it is NEMA size 00. It has three heaters which may be set to one of four current settings. Kind of a transitional type of heater between the single value heaters of old, and the potentiometer adjustable heaters on today’s starters.
Cutler-Hammer NEMA Size 00 Starter
Other Issues
Heater Class
A-B Heater Interchangeabilty
NEMA Style
While NEMA size refers to the electrical “size” of the contactor as described in the previously referenced NEMA tables, NEMA style refers to the size of enclosures used to house Starters.